Please find the estimation of your small transformer.
Primary impedance Z = 120V / 0.0353 = 3399Ω
Z = 2 x pi x 60 x Lp+DCR
This is not correct. The correct relationship is:
\[Z= \sqrt{(2 \pi 60 Lp)^2+(DCR)^2}\]
Primary Inductance Lp = (3399 – DCR) / 2 x pi x 60
Approximate DCR = 1500 (For small transformer < 3VA)
Lp = 5.04H
As I said in post #27, this is a 5VA transformer. The measured primary DCR is 138 ohms. The measured secondary DCR is 2.01 ohms.
The correct expression for Lp is:
\[Lp=\frac{\sqrt{Z^2-DCR^2}}{2 \pi 60}\]
Even if DCR were 1500 ohms (which it isn't), the result of the correct calculation would be Lp=8.09H, not 5.04H. Using the measured value of DCR, we get Lp ≈ 9H
Voltage ratio = 120/13.9 = 8.633 Square of voltage ratio 74.53
Secondary inductance Ls = Lp / 74.53 = 68mH
The correct calculation of the secondary inductance gives Ls = 9/74.53 = 121mH, which is not too far off my measured value of 135mH
All these calculations verify the small effect that the real part of the impedance has on the magnitude of the impedance. This was earlier determined by the ratio of the apparent power to the true power as discussed in post #27.
For the primary side (with the secondary opened), using a resistor of 9.7 ohm, I`ve got 241 mV (24.85mA) with a phase shift of -63 and the voltage in the terminal of the transformer was 228V.
And for the secondary side, I`ve got 0.96V around the resistor (98.97mA) with a phase shift of -62. The voltage in the terminal of the transformer was 18,5 V.
Something is wrong here. Your turns ratio, using the rated voltages, is 230/18 = 12.78
The ratio of the exciting currents, if the applied voltages are in the proper ratio (the turns ratio), should be the same as the turns ratio. But the ratio of your exciting currents is 98.97/24.85 = 3.98. This is not even close to 12.78.
You really need to measure the open circuit secondary voltage with 230 volts applied to the primary, and use that as the voltage applied to the secondary for the exciting current test.