I wonder:
What is the inductance when idle current is 10% of rated current?
What is loss factor in W/kg of CRGOS used?
Were edges processed so as to prevent intralayer lamination shorts?
Right....!Yes indeed, ten percent of full rated current would be HORRIFIC for an inverter.
Just imagine 500VA of continuous wasted idling power loss for a 5Kw rated inverter running 24 hours per day.
A more reasonable and readily achievable figure would be 10VA to 30VA for a home wound inverter transformer of this size, and 50Va to 80VA fairly typical for a similar sized (minimum cost) commercial inverter transformer.
Batteries are always the most expensive part of the system, and its always more economical to spend a lot more on copper and steel for the new home built transformer, than adding the required extra amp hours to the battery.
Its not commercially viable for the inverter manufacturers to do this, but we certainly can !
And end up having a much superior and more efficient inverter as a result.
Inverters have high dV/dt and usually use ferrite. Transformers with CRGOS have far greater mu and lower BW thus are ideal for sinusoids. Using this for an inverter will create more eddy current losses than sine excitation transformer losses. Perhaps you want to specify your design expectations?I guess first two parameters will be known later, I have painted using oil paint and some will stay between lamination layers
--- Updated ---
Right....!
YesA sine wave inverter is a 230v 50Hz sinusoid, and there is no high dv/dt in the transformer. Only a very low residual of the original pwm frequency, which we are trying to filter out anyway.
The associated choke in series with the primary will have a very high series impedance at the pwm switching frequency, and a very low series impedance at 50Hz. That is its function
This is a false assumption.Yes indeed, ten percent of full rated current would be HORRIFIC for an inverter.
Just imagine 500VA of continuous wasted idling power loss for a 5Kw rated inverter running 24 hours per day.
True, the losses will certainly be lower, but more difficult to measure directly at the initial testing stage where you only have a bare transformer and no pwm driver.This is a false assumption.
The magnetization current to create the mutual coupling in a transformer is a reactive current and the real losses depend on the resistance. So the real idle losses are much lower.
I am having difficulty, fully grasping how the hoop and in general motorized winding machine works, I think this hoop is a manual way to do the same thing, it will enforce winding in radial direction. i am wondering if the hoop is dangling cuz its center is not arrested then how could it achieve that... there are few more items though ...in motorized machine it appears like the wire is sliding over ring during unwinding process, it can damage the wire.Well done finding the wire !
First the suggested method of winding, so you can get yourself set up.....
Many other people have been through this exact same exercise, and the general consensus is, that the easiest way to do all this is to first construct a suitable winding "hoop". This can be an old bicycle rim (least suitable), a child's plastic hoop (best if you can find a hoop) or a length of split black plastic irrigation pipe (annoyingly floppy but possible).
The idea is that first the empty hoop is looped through the toroid, like two links in a chain. The toroid sits on the very edge of a work bench on a firm "V" extension, and the hoop hangs supported from a high hook.
Wire is first loaded onto the hoop, then can be progressively unwound from the hoop as each turn on the toroid is completed. The pictures below should make all this a bit more clear:
--- Updated ---
The above pictures were shamelessly stolen from a thread on The Back Shed Forum.
https://www.thebackshed.com/forum/ViewTopic.php?FID=4&TID=14639
If you are wondering what a "Warpverter" is, its a non PWM pure sine wave inverter of my own design, that uses four separate low frequency square wave inverters with the outputs combined in series to produce a very finely stepped 230v waveform that has less than 1% THD.
That thread has some pretty good practical information about winding large toroids, and inverter construction in general.
Yes I understand that.The hoop is not motor driven,
Yesconvenience and least damage to the wire.
I just want to fix the hoop and figure out a mechanism to unwind like machines... It will yield a better quality turns. This is my first winding, I am completely unaware of pits & fall doing it, its very likely that I will end up very ugly windings...Knowledge and experience has been shared, and the suggested method developed over time works, and has slowly been improved upon by multiple different people over many years.
What it means is transformer under full load will have greatly reduced efficiency, Its something cannot be avoided.Thus depending on the steel, for the VA measured at idle, losses could be anywhere from 20% to 80% of the VA measured - depending on the steel - and the level of excitation.
OkDóh - the flux does not change with load, it is fixed by the applied volt seconds, 230Vac, 50Hz in this case.
Full load efficiency is most largely affected by the thickness of the wires