Interestingly non of the contributors in this thread seems to refer to the simple voltage divider configuration, everyone is suggesting a constant current source topology and linearization methods presuming a linear resistance measurement.The general idea Pt100+R1 will stay.
The voltage divider circuit is nevertheless a valid option for a simple RTD thermometer, specifically if used with ratiometric measurement. But it's necessary to correct the nonlinear voltage divider characteristic in a foregoing calculation
Code:
V1 = Vref*Rpt100/(R1 + Rpt100)
A basic advantage of the circuit is that besides the RTD itself, accuracy depends only on reference resistor and ADC.
Only reasonable if also used as ADC reference.The special power supply only for Pt100 might be added.