Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.
Commercial WYE WYE Transformers do not provide access to all 6 terminals of the primary or secondary windings. They have the common terminal connected internally and brought out as a single connection, so it is not possible to do what you propose. However, if all 6 terminals of, say, the secondary were available, the result would be an unsymmetrical phase relationship with the 3 phases separated by 60 degrees instead of the normal 120 degrees. If the normal phase sequence is A-B-C, then the new (Unsymmetrical) phase sequence would be A-C-B, with a 240 degree gap between C and B.