These have to be monitored with meters. Frequency is controlled by engine rpm. Voltage is controlled by an AVR which will have some provision for adjusting the voltage. The adjustment may be a potentiometer or pushbutton or keypad.1) How to match the frequencies & voltages of two generators accurately ?
There will be circulating currents. This means that current will flow from the higher voltage to the lower voltage, and this results in wasted power. Since a generator is essentially a power source with a very low output impedance, the circulating currents can be very large even for small differences in voltage.Because there is some variation or voltage drops in the output voltages of the generators , for e.g : 396 V to 400 V ...... if one's voltage is 398 V at a particular instant & other's 404 V then, what might happen ?
Again wasted energy.Also, same with the frequencies, then, what might happen ?
An oscilloscope could be used but other methods are often more practicable. See my reply and chuckey's above for one method.Should we check this out with the help of oscilloscope ?
Yes.if all the outputs of all the generators going to zero & going to max. 1 value at the same time , then, it means the generators phases are synchronizes , Am i correct ?
The three phases of the same generator have a fixed relationship so that if one phase is in sync with another generator, the other two will also be synchronized. However, the phases have to run in the same order for the two generators. The three phases are often called R, B and Y for Red, Blue and Yellow. If the phases of one generator are in the order R-B-Y, then the other generator also has to run in the same order. All three phases are usually monitored while synchronizing to make sure they are in the same order.And, then check to all of the three phases one by one ......... ?
Yes. But remember that it's not the names of the phases that are important, but the order in which their voltages change.If one is in R-B-Y configuration then the other & also the third one should had the same configuration ? am i correct ?
If I understand your question correctly, it's because they don't always have the same load. A 3-phase motor will always draw the same current from each phase, but each of the phases may be given separate single-phase loads such as lighting, household appliances like TVs, computers, etc. An important (and often difficult) job of power distribution technicians is to try to balance the loads so that each phase has an approximately equal load.why there's always some variation in the per phase amps of a 3 phase system ?
It;s because a 3-phase system is more efficient and more convenient for many applications. For example, a 3-phase motor can be simpler than a single-phase or 2-phase motor. Rectified 3-phase voltage has less ripple and is more easily filtered. Some applications may not require any filtering. Sending 3-phase power over a distance requires smaller and lighter wires because the load currents are distributed over 3 lines.why we don't use the two phase system ?
It's the AC frequency, not the actual rpm, that's important. The frequency is determined by the rpm and the number of poles.What should do when rpms are not getting matched of the two generators ?
if one's rpm is 1000 rev/m & others 1500 rev/m ...... what else we can do to synchronize their rpms ?
Can I ask if this is related to a particular project or is a general question ?. As if related to a particular project, please, provide the all specifications of the machine to be supplied from, as it may lead some other better guidance. And if a general question then it is ok.What things should be considered when paralleling 2 or 3 generators ?
should run any generator to its 80% output power ? & not exceed that limit .......... Is it a right thumb rule