Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

What cable size should be used for a 50KW load ?

Status
Not open for further replies.

danishdeshmuk

Advanced Member level 1
Advanced Member level 1
Joined
Aug 17, 2011
Messages
426
Helped
35
Reputation
70
Reaction score
35
Trophy points
1,308
Activity points
4,001
What cable size should be used for a 50KW load ?

Can i use a 50 mm2 , 3.5 core cable for that (where neutral is half i.e. of 25 mm2) ?

thanxXx
 

In a three phase system p=1.732x3xVxIxCOS@
When load is given 50KW
Then I=50000/1.732x3x415x.8 =86A or near about
You can take a cable of 100A capacity, that's roughly 50 mm square in copper ....
 

it means i'm right . 50 mm2 cable of 3.5 cores is right

inside the 3.5 core , 50 mm2 cable , what would be the size for each of the 3 phase and for the neutral ???
 

Hallo danishdeshmuk,

in the attachment you two tables about cable size and motor current.

I hope it helps.

Regards

Rainer



PS: The pictures are copies from "Klöckner Möller, Schaltungsbuch 1964; Seite 143 und 144".
 