What about the condition of the motor ? OR its attached mechanical things , system

Status
Not open for further replies.
If you have the option, this should help to narrow down the problem.

Can i use a 22KW Drive to narrow down the problem Or should i have to use the same capacity drive for doing that ?

thanks
 

what happened , no answer yet , answer it guys plz
 

An inverter of higher power can be always used with a smaller motor, but you should either parameterize it for correct motor currents or watch the motor currents carefully during the test.
 

yeah i would definitely parameterize the drive with that smaller motor ........ its rated voltage , rated current , rated rpm , etc .

Are you talking about it only ?
 