Oct 10, 2012 #21 P phatcreators Full Member level 5 Joined Sep 2, 2011 Messages 315 Helped 24 Reputation 48 Reaction score 24 Trophy points 1,298 Activity points 3,458 FvM said: If you have the option, this should help to narrow down the problem. Click to expand... Can i use a 22KW Drive to narrow down the problem Or should i have to use the same capacity drive for doing that ? thanks
FvM said: If you have the option, this should help to narrow down the problem. Click to expand... Can i use a 22KW Drive to narrow down the problem Or should i have to use the same capacity drive for doing that ? thanks
Oct 14, 2012 #22 P phatcreators Full Member level 5 Joined Sep 2, 2011 Messages 315 Helped 24 Reputation 48 Reaction score 24 Trophy points 1,298 Activity points 3,458 what happened , no answer yet , answer it guys plz
Oct 14, 2012 #23 FvM Super Moderator Staff member Joined Jan 22, 2008 Messages 53,107 Helped 14,792 Reputation 29,871 Reaction score 14,291 Trophy points 1,393 Location Bochum, Germany Activity points 301,057 An inverter of higher power can be always used with a smaller motor, but you should either parameterize it for correct motor currents or watch the motor currents carefully during the test.
An inverter of higher power can be always used with a smaller motor, but you should either parameterize it for correct motor currents or watch the motor currents carefully during the test.
Oct 15, 2012 #24 P phatcreators Full Member level 5 Joined Sep 2, 2011 Messages 315 Helped 24 Reputation 48 Reaction score 24 Trophy points 1,298 Activity points 3,458 yeah i would definitely parameterize the drive with that smaller motor ........ its rated voltage , rated current , rated rpm , etc . Are you talking about it only ?
yeah i would definitely parameterize the drive with that smaller motor ........ its rated voltage , rated current , rated rpm , etc . Are you talking about it only ?