Voltage regulation in Finland seems to be similar to German electric network. Voltage regulation information is not so easy to find, but google found several finnish language student thesis and I collected following information from those. Base distribution network is at 110kV level and local electric stations transform 110kV to 20kV or to 10kV. 20kV is used with overhead lines and 10kV is typically used in cable network. 110kV voltage regulation requirement, when average rms voltage is monitored in 10 minutes intervals:
105-123 kV 95% of the time
100-123 kV 100% of the time
Typical measurement period is one week. This is what local electric (sub)station gets. There is on-load tap changer in the 110kV/20 kV or 110kV/10kV trafo and it is where local voltage regulation is done. There is no regulation done in 20kV/0,4kV (or in 10kV/0,4kV) trafo. Typical on-load tap changer has ± 9 x 1,67 % taps. This is for 20 kVsecondary, but we can assume similar functionality for 10kV secondary voltage.
How many households or x/400V transformers are covered with one tap changer? I calculated average ballpark number for Helsinki. There are 23 "110kV electrical stations" (at least few years back) in Helsinki. If assuming, that there is one 110kV trafo per station and 660000 citizens in Helsinki, about 30000 citizen are covered with one tap changer.
Helsinki utility company tend to use 31,5 MVA and 40 MVA transformers. If typical power rating of 10kV/0,4kV transformer is 500 kVA or 1 MVA, we can say that tens of those transformers are behind one tap changer. Following image shows (nominally) 230V rms at my home. Values are 1 minute averages. It is possible to see, that voltages goes higher late evening, and voltage is stepped lower. On the morning, voltage is stepped higher.
This shows one of the tap changes, when rms values are calculated with 2 seconds interval.