Hey Guys,
I'm troubleshooting a steel cable pusher and need some advice.
The 2.2kW motor is driven by a Lenze I550 VFD. It is powered via a 10a plug, as it is used in different locations. (Tripping RCD on different Locations)
The pusher was running fine for half a year it started tripping the rcd when either plugging it in or when the motor got too much mechanical pressure back. ( If I shut the lead off, plug in, and turn the lead live it's fine and will then only trip when too much mechanical pressure)
So far I disconnected the motor but rcd still tripping. I disconnected the Main Earth to determine how much voltage the VFD got against Earth and It's over 40V.
If I attach a second lead to increase the resistance against Earth rcd won't trip. Earth connections seem to be all right.
Was thinking EMF may be faulty? If so how can I determine that?
Thanks in advance for your input!!!
I'm troubleshooting a steel cable pusher and need some advice.
The 2.2kW motor is driven by a Lenze I550 VFD. It is powered via a 10a plug, as it is used in different locations. (Tripping RCD on different Locations)
The pusher was running fine for half a year it started tripping the rcd when either plugging it in or when the motor got too much mechanical pressure back. ( If I shut the lead off, plug in, and turn the lead live it's fine and will then only trip when too much mechanical pressure)
So far I disconnected the motor but rcd still tripping. I disconnected the Main Earth to determine how much voltage the VFD got against Earth and It's over 40V.
If I attach a second lead to increase the resistance against Earth rcd won't trip. Earth connections seem to be all right.
Was thinking EMF may be faulty? If so how can I determine that?
Thanks in advance for your input!!!