Continue to Site

Welcome to EDAboard.com

Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

ups dry battery replace with lead acid battery

Status
Not open for further replies.

dheerajyoti

Newbie level 1
Newbie level 1
Joined
Feb 22, 2013
Messages
1
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,286
please tell me any one,i have 230V 1000va APC smart ups(it have 2x 12v 12 Amp dry battery) can i use 2x 12v 100 Amp lead acid battery,it can charge properly and increase backup............. i am waiting for reply anyone............thanks.
 

please tell me any one,i have 230V 1000va APC smart ups(it have 2x 12v 12 Amp dry battery) can i use 2x 12v 100 Amp lead acid battery,it can charge properly and increase backup............. i am waiting for reply anyone............thanks.

You can, but you need to use some additional charger. Your UPS charge batteries with 0,7A and you need now 10A @24V.

And check UPS construction and heatsinks, maybe he cant handle longer working time under higher loads, he is not designed for this, sometimes is needed to replace existing heatsinks with bigger and better.

Maybe one or several additional cooling fans. Keep in minds that you want to use device against manufacturers recommendetions.

;-)
 

Status
Not open for further replies.

Part and Inventory Search

Welcome to EDABoard.com

Sponsor

Back
Top