No.230V mains is about 330V peak which powers the inverter for the bulb. With a modified sine wave the peak voltage is only 230V, so the inverter will produce a lower voltage which will not strike the tube.
Frank
Power is not 12V 7.5A. Power is Watts or VA. A battery is also not 7.5A, it might be 7.5Ah which is its capacity, not its maximum current.The power of ups is 12V 7.5A.When i connect bulb directly bulb works normally but when i connect it in output terminal of ups it turned off within a second.
Why would a UPS need a minimum load? It has a very small low power battery which would produce only 48W for 1 hour.I meant that the UPS needs to run minimum load . CFL has about 10-30 watts only , ..
For a load of 720W the 12V battery must supply 60A. A lead-acid car battery with a capacity of 60Ah can supply 60A at 12V for 7.5 minutes, only when the battery is new.75 A with 12 volt battery can provide about 720 watt for 7.5 minutes . right ?
Yes. The battery voltage is dropping and at 7.5 minutes it drops to 12V. At 25 minutes the battery is dead at 11V.Is 12V/60Ah battery can provide only 7.5min running time at 720W load?
Yes. The battery voltage is dropping and at 7.5 minutes it drops to 12V. At 25 minutes the battery is dead at 11V.
Simply look at the graph I posted in post #12. C is the capacity of the lead-acid battery in Ah. The battery voltage drops below 12V in 7.5 minutes when the current is C.How can i calculate it ?