I have had a problem with relay coil snubbers, the fault was that when the relay was energised it would not de-energise. In the end it was due to the change of inductance of the relay coil when the armature moved and completed the magnetic path.
The circuit was a triac that had a slugging circuit on its gate, so after 4 seconds after the supply came on , the triac was switched off and dropped out a AC plug-in relay (motor start circuit). As a precaution, I put a .047 MF cap across the triac. When the supply came on, the relay pulled in, after 4 seconds - nothing. The triac must be faulty so I changed it, same again. it was only when I replaced the relay with a resistive load and measured the voltage I figured out what was happening! When the triac was off I had 160V across the relay (240 V mains).
Frank