Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Single phase transformer

Status
Not open for further replies.

emperror123

Member level 5
Member level 5
Joined
Dec 11, 2010
Messages
86
Helped
1
Reputation
2
Reaction score
1
Trophy points
1,288
Activity points
1,880
to all,
i were facing a problem on single phase transformer on calculation part.
i been sketches out the single phase transformer equivalent circuit.
and some information given
f = 60hz
s = 20kVA
V1 = 2400v
V2 = 240v
R1 = 3Ω
R2 = 0.03Ω
X1 = 6.5Ω
X2 = 0.07Ω
Xm = 15kΩ
Rc = 100kΩ
lagging P.F. = 0.8

and here the problem come. i were trying to solve the problem.
which is
i got Xeq1 = R1 + a^2R2 = 13.5Ω, and Req1 = X1 +a^2X2 = 6Ω
i got primary voltage is V1 = 2400V and V2' = aV2 = 2400V
how do i calculate the primary current and secondary current?
and also the source voltage.

thank you and much appreciate with your help to solve the problem
 

...i got Xeq1 = R1 + a^2R2 = 13.5Ω, and Req1 = X1 +a^2X2 = 6Ω...

should be as?

Req1 = R1 + a^2R2 = 13.5Ω, and Xeq1 = X1 +a^2X2 = 6Ω

is it ?
 

SRIZBF:
sorry, is a typo error. shud be the same as u say

atripathi:
shall i need to include Xm and Rc into the formula to calculate the Ip or Is?
the source voltage got any formula?
 

I would assume Source Voltage as 2400V (equal to V1, in specifications mentioned by you)
Yes, you need to include Xm & Rc into current calculations Ip. Ip=Io + Secondary (or load ) current reflected in primary; here Ip is current drawn from source
 

how could i get voltage load, it do not gave any resistance load in circuits
 

how could i get voltage load, it do not gave any resistance load in circuits
You didn't tell the exact exercise text, but you're asking for a secondary current, so there should be a load, isn't it? The only hint for the load I found is the P.F. number, but I think you'll need more information about the load, I think.
 