I wanted to get the forums thoughts on Simulating a typical 60Hz Power System as 6Hz. 10 times less than the actual system frequency.
The motivation for this is to be able to simulate at only 0.005 time step (200Hz) and run real-time on a typical Computer.
At the 0.005 timestep there would be about 33.3 samples of a 6Hz waveform which would be adequate, however if simulating 60Hz it would only be 3.3 samples oer waveform which is unacceptable.
The Power System consists of 4-5 (4-50MW) Generators, Induction Motors, DC Loads, Power Converters. Exact simulation detail is not required, only basic dynamic operation for Training/Learning Purposes.
(Phasor simulation was also considered, however the 6Hz solution would provide better real-time domain waveforms.)
-How would making this conversion effect the various simulation parameters when comparing it to a full 60Hz simulation at 10us time step?
-How would the impedance/controls change etc? (Controls are mostly done RMS)
The motivation for this is to be able to simulate at only 0.005 time step (200Hz) and run real-time on a typical Computer.
At the 0.005 timestep there would be about 33.3 samples of a 6Hz waveform which would be adequate, however if simulating 60Hz it would only be 3.3 samples oer waveform which is unacceptable.
The Power System consists of 4-5 (4-50MW) Generators, Induction Motors, DC Loads, Power Converters. Exact simulation detail is not required, only basic dynamic operation for Training/Learning Purposes.
(Phasor simulation was also considered, however the 6Hz solution would provide better real-time domain waveforms.)
-How would making this conversion effect the various simulation parameters when comparing it to a full 60Hz simulation at 10us time step?
-How would the impedance/controls change etc? (Controls are mostly done RMS)