The current limit on cable is due to the cables resistance and the temperature rating of the insulation and how the heat is conducted away from the outside of the cable. So the 111 Amps should be also equated with the temperature rise of the cable, so if you run the cable in a hot place, its current rating will be lower and at the melting point of the insulation its zero. Conversely if the cable is buried in a marsh where the heat can be conducted away, it can carry more current.
If you have say 10 m. of this wire running at 100A, it might drop .8V so at mains voltage, you would get 230V - .8 = 229.2 ~ 99.7% of the input volts. If the supply was 12V, it would still drop .8V, you would get 11.2V or 94% of the input voltage, so at 12V you need BIGGER cable, not for the current rating but for the voltage drop.
Frank