U will get an equivalent ac source which can be calculated as follows:
Assume 2 sources with same fundamental frequency: V1cos(wt+θ1) and V2cos(wt+θ2).
In phasor notation: V1Lθ1 and V2Lθ2. [L stands for angle]
Using phasor addition: V1Lθ1 + V2Lθ2 =V3Lθ3 ...........(say)
Let:
X=V1cos(θ1)+V2cos(θ2)
Y=V1sin(θ1)+V2sin(θ2)
V3=√(X²+Y²)
θ3=arctan(Y/X) [arctan means tan inverse function]
Or simply, u can calculate this graphically using vector addition method for adding 2 vectors: V1Lθ1 and V2Lθ2.
For detailed explanation to how this phasor addition is done, refer some good book related to electrical networks.
Depends on the AC sources...But if i connect two 230v AC sources in series. What will happen..?
will any problem occurs ?
No problems, provided you have taken into account the considerations mentioned by FvM. And the result could be 460v AC if the two sources were in phase and nearly zero volts of the two sources were 180 degrees out of phase (I.e. You swapped two of the leads).According to theortical basis i understood. But if i connect two 230v AC sources in series. What will happen..?
will any problem occurs ?