Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Reading Siemens logo 12/24Rco relay status on raspberry pi

Status
Not open for further replies.

hanif

Full Member level 4
Full Member level 4
Joined
Feb 14, 2007
Messages
203
Helped
44
Reputation
88
Reaction score
30
Trophy points
1,308
Location
Pakistan
Activity points
2,442
Hello every one, i have a task to read Siemens logo 12/24Rco relay status using raspberry pi. The logo is place 3m away from raspberry pi. One option is to connect GPIO pin by pullup resistor but Vcc for pin is 3.3V and there may be some voltage drop occur as logo place 3m away from pi.

Can anyone help me to resolve this issue

Fiemd.png
 

It shouldn't be a problem.
The resistance of 6m of wire (3m x 2) is very low compared to 10K so the voltage will go from almost 3.3V to almost zero when the relay operates.
If noise pick-up is a problem, add a resistor of say 100 Ohms in series with the relay contacts and add a capacitor from 'GPIO IN' to ground at the pi end of the cable. I would suggest 100nF as a good value and do not go more than about 1uF.

Brian.
 

It shouldn't be a problem.
The resistance of 6m of wire (3m x 2) is very low compared to 10K so the voltage will go from almost 3.3V to almost zero when the relay operates.
If noise pick-up is a problem, add a resistor of say 100 Ohms in series with the relay contacts and add a capacitor from 'GPIO IN' to ground at the pi end of the cable. I would suggest 100nF as a good value and do not go more than about 1uF.

Brian.

Thank you for your prompt response. Can you suggest me the type of cable should i use for above mentioned task like shielded etc
 

It depends on where the cable has to run. If it passes places where it is likely to pick up strong interference it would be best to use a shielded cable but otherwise any cable that has sufficient insulation to protect against outside voltages should be OK. The current is very small so you could use thin (7/.02) hook-up wire for example. If you use two separate wires, twist them loosely as this will help to reduce noise pick-up.

In one job I did, the switch contacts were nearly 100m away and it still worked fine.

Brian.
 

Hi,

The above circuit is possible.

Here my recommendation to improve it:
* switch 24V.
* feed the switched 24V through the cable to the raspberry (this improves signal to noise ratio)
* use a resistive voltage divider to get valid raspberry input levels (maybe 10k /1k, this reduces RPi input signal impedance)
* use a capacitor at the RPi input to suppress noise
* use two diodes for RPi input protection.

This gives a more reliable data "communication".

Klaus
 

... but be careful that the ground on the Pi is at the same potential as the ground on the 24V supply. Under no circumstances should you use the potential divider method if the relay is powered from equipment that is not isolated from the AC mains. The relay method provides voltaic isolation, if it's there for a reason I would stay with plan 'A'.

Brian.
 

Hi,

if the relay is powered from equipment that is not isolated from the AC mains.
I assume the relay is inside the PLC. If so, then you don´t have acces to the coil. Only the contacts are accesable..and they should be isolated.

Klaus
 