Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Question about Transformer

Status
Not open for further replies.

panda1234

Full Member level 2
Full Member level 2
Joined
Jan 22, 2015
Messages
125
Helped
4
Reputation
8
Reaction score
4
Trophy points
18
Activity points
1,172
Hi,
Why we use low voltage side for no load test and use high voltage side for short circuit test.
thanks
 

Hi,
Why we use low voltage side for no load test

Since the secondary of the transformer is open, the primary draws only no-load current, which will have some copper loss. This no-load current is very small and because the copper loss in the primary is proportional to the square of this current, it is negligible. There is no copper loss in the secondary because there is no secondary current.

Hi,
Why we use high voltage side for short circuit test

The supply voltage required to circulate rated current through the transformer is usually very small and is of the order of a few percent of the nominal voltage and this 5% voltage is applied across primary. The core losses are very small because applied voltage is only a few percentage of the nominal voltage and hence can be neglected. Thus the wattmeter reading measures only the full load copper loss.
 