Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Looking for info about Earth Leakage Circuit Breaker [ELCB]

Status
Not open for further replies.

marov

Newbie level 6
Newbie level 6
Joined
Dec 5, 2010
Messages
11
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,377
Hi

I just need to know more about elcb (earth leakage circuit breaker)

Does it protect against overload or only against short circuit?
 

Re: Inquiry about (ELCB)

Earth leakage circuit breaker generally check that supply wire (L) and return wire (N) has equal current,
ie current from L has no connect to earth . (1-Phase device )
Overload and short circuit protective device are different parts, they can be inbuild to ELCB device.

ELCB_NoLe.jpg ELCB_IsLe.jpg

3-phase working principle is similar,
check sum of vectors L1+L2+L3+N , if equals zero = no gleak to ground.

General.............
Earth leakage circuit breaker - Wikipedia, the free encyclopedia

Example device...........
**broken link removed**

Short info...........
This is the Pathumthani
 
Last edited:

Re: Inquiry about (ELCB)

Kak111 has described an RCD, that is a Residual Current Detector. Its a modern thing. If you want it to trip on overloads you need an RCBO. An ELCB was an old fashioned set up with a breaker with a trip coil which needed 50V to trip it. This trip coil was wired between the earth return of an electrical installation and the true earth. When the earth leakage current of an installation (which flowed through the coil) got too high, the breaker tripped. Problem is that any faulty installation earths that shorted or are connected to a true earth also shunts the trip current away from the trip coil coil so stops the ELCB working.
Frank
 

Re: Inquiry about (ELCB)

Thanks for the information guys..



What pushed to that question that i found in a panel MCB connected to the power source then the 4 poles of the MCB are connected to the ELCB which is connected to smal breakers for power distribution....

The question is if the ELCB can protect from short circuit and overload why some designs require to use both mcb and elcb at same time?! What is the role of the mcb then?
 

Re: Inquiry about (ELCB)

So how can we differentiate between an elcb and rcbo?
 