Do you guess about the power dissipation of the Mosfet?TL;DR I'm not sure why the cause of heat is a misunderstood. It shows high power spikes on the edges which are due to all node capacitance from Coss of FET , and clamp diode.
By some limited choices in LTspice I reduced the FET average power to 170 mW (1.2kWpk) using a low Q FET and a low Q clamp diode.
View attachment 197738
Leading edge power spikes (green) were observed in the initial simulation provided and reduced with my low Q=CV choice of semi's. Rated > 600V.Ah yes - we can't see the layout - turn off spikes will easily kill the mosfet when you get above 180VDC supply - a good scope would see this straight away
explains sort of OK operation at lower Vcc
--- Updated ---
Also - at the higher Vcc - RF can easily get into the controller and upset things.
supply voltage is 150Vac.The snubbers are too small for HV operation - as said just above - if we can see G-s and D-S at turn off at 150V - then the issue will reveal itself
( waveforms at turn on too will be useful )
I dont have any idea about Vs peaks...supply voltage is 150Vac.
Vgs: (Volt/Div divide by 2) => example: Min Volt is 57/2 = 28.5V
View attachment 197771
View attachment 197772
Vds: (Volt/Div *5)=> example: MAX Volt is 38*5 = 190V
View attachment 197773View attachment 197774
I am changing shunt resistor value to 0.54 ohm.
Vs:
View attachment 197775
I calculated the probe attenuation for you... and wrote it in front of each image as a multiplication or division. Vsource-gnd doesn't have probe attenuation.Last 3 of your pics unlabeled.....? What test point are they ? What are we looking at ?
You are violating Vgsmax specs -
View attachment 197777
What is the sampling rate scope screen shots acquired ? Scope probes set to 10X right ?
Regards, Dana.
This one especially does not make any sense. Suggests some major issue with how you're probing it, or some huge parasitics somewhere in the circuit itself.supply voltage is 150Vac.
Vgs: (Volt/Div divide by 2) => example: Min Volt is 57/2 = 28.5V
View attachment 197771
I used an insolated probe.This one especially does not make any sense. Suggests some major issue with how you're probing it, or some huge parasitics somewhere in the circuit itself.
From your schematics, it seems that the circuit is supplied from a bridge rectifier, so unless you use an isolation transformer on the AC supply, you can't connect your scope GND anywhere on your circuit. Are you using an isolation transformer, or a differential probe....?