Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Installation of a three phase 1.1 kW pump/motor to a PLC

Status
Not open for further replies.

electronZ

Member level 2
Member level 2
Joined
Apr 11, 2010
Messages
43
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,286
Activity points
1,602
I have divided a big task into small sub-tasks :)

As the title says, I am now focusing on installing a three phase 1.1 kW 220-240/380-480 V @ 50 Hz pump to a PLC unit.
Basically how I see it, is the PLC de/activates the relay/contactor which turns on/off the supply to the pump.

I need advise and guide throug this, thank you :)

I see it like this:

1. Calculate the supply current used by the pump
2. Choose cable
3. Choose a relay
4. a fuse?

1. Calculate the supply current used by the pump
I understand that it is recommended to use the highest voltage supply? why? :/
That means : (1.1 kW)/(480 V)= 2.29 A ~ 2.3 A

2. Choose cable
I got a bit lost here... Found a lot of tables, some equations, and I really got lost. I cant see how to determine the voltage drop, I read around 10% for motors?
I got a value of 1.5 mm^2 3-5 meter long copper wire. How does that sound? Another way to find a cable?

3. Choose a relay
Not started yet...will be more than happy for ideas.

4. a fuse?
Is it necessory? maybe between the mains and the relay?

Thank you for your time, I appreciate it.. and many others :)
 

1. Using the high voltage results in thinner, cheaper cables.
2. I think (in the UK at least) 10% should be 2.5%, but 1.5mm^2 looks OK.
3. Motors when they start have an inrush of 5X running current - check this on relay current ratings.
4. The best way is to use a MCB (minature circuit breaker) as close to the incoming mains supply as possible to feed only this circuit. Get a Motor rated one (type C or K?), this allows for the big inrush starting current but over a long time (10seconds) offers close current tripping - 3A. A fuse will sag due to the inrush currents wearing it out and will fail in time.
Frank
 

Here is application note from ABB : Motor starting Solutions...........

**broken link removed**
 