Hello Friends,

I need some help from you all in MODBUS protocol implementation through RS-485.

I am getting some weird type response from a slave (energy meter of reputed make) though I send proper query through PC Modscan32 software. I am herewith attaching a snapshot of respective image. Please try to find some time to help me out because my stuck now and not getting any enough help around.

Query : 01 04 00 00 00 06 78 1F
Response : 01 10 68 C5 BA D6 C9 9E 5428 D5 D0 D7
(function code 0x10 !!! actually I was expecting 0x04!! why this???)
 

hello,


it seems than return code 10h => 16 Return Slave NAK Count
if your device support all modbus protocole

ModiconModbus Protocol
Reference Guide
Maybe you can do some test with QUERY DATA loopback


and response


 
Thank u for reply.

I am going to check the said loop back test. Beforeion that i need to mention that if I send MODBUS query over USB to RS485 converter then Slave shows exact response but when I send it through RS232 to RS485 conerter of different make then I gets the improper response i.e Function code 0x10 (16 in decimal).

Is this direction pin's (DE/ RE) issue of MAX 485??
 

is it a true RS485 mono paire or like RS422 2 paires, one for transmit one for receive..
RS232 must manage RS485 protocole (some silence to manage..etc..) .It is not only hardware signal conversion
common mode to differential mode..

How is made your hardware RS232/RS485
is it an industrial interface ? or just level translator devices.

What about the cable length and load on the RS485 bus .. terminal resistor value.
 