Try to isolate the ground.
As already discussed by others, the problem is most likely common mode interference. RS485 based fieldbusses like PROFIBUS are using optical isolation for a good reason. If you don't provide isolation, a ground connection along with the twisted pair, either by the cable shield or a separate ground wire is mandatory. If you additionally use common mode chokes, the interferences can be usually brought under control.
If a ground connection of sufficient cross section is carried along with the signal lines, there won't be much low frequency common mode interferences left. Problems may arise if the power circuit has missing or incorrect ground wiring and a large common mode voltage difference between both RS485 peers exists. In this case, it's in fact difficult to work without isolation. But you can still try with a larger toroid core of high µr ferrite, putting several turns of the RS485 cable (including ground) through it.I know and I don't want to use bulky solutions, but the signal chokes are genereally tuned to work in the upper MHz range. I don't know how much will they be effective in the kHz range.