problem in winding of a motor of any type
Your short question includes material for a very thick book, i think.
Look this first...
At the request:
I give here short and simple instructions to check 3-phase induction motor with contactor control...
The motor is in operating place
- fuse(s) is blown or overcurrent relay tripped
1. Check voltages of all supply phases before fuses (phase to phase)
voltages should be same (+/- 2%)
Disconnect supply to motor control ( Main switch OFF )
Replace fuse(s) if there is blown one(s), reset overcurrent relay
2. check all motor contactors
-wiring connections are tight
-when closing contactor by pushing with hand
-- all contacts closes and closed resistance is zero ohm
3. check that motor overcurrent relay inside resistances in phases are equal
--check connections
4. all fuses are in place, overcurrent relay is not open
5. Disconnect motor cables. ( Now test for motor control and supply )
6. check that all connections and cables are safe for the start-up.
Connect supply to motor control ( Main switch ON )
7. Try to start motor.
8. Check that contactors are operating correct.
9. Measure voltages phase to phase in motor supply terminals.
10. If above is OK. ( Motor terminals have correct voltages )
Disconnect supply to motor control ( Main switch OFF )
11. check motor insulation to ground
- Dmm high-ohm range , measure phase wires to ground.
....should be megaohms.
12. Open motor connection box
- check all winding connections in motor
13. Check motor winding resistances (U-V), (U-W) and (V-W).
- Dmm lowest-ohm range ....all should be same (+/-2%)
14. Check that motor is free to run (not stucked)
-- if it is possible , remove the motor load.
15. Connect motor cables to contactors
16. check that all wirings are connected and
all connections and cables are safe for the start-up.
17. all fuses are in place, overcurrent relay is not open
18. Try to start motor.
19. If motor dont start, STOP immediately .... >> goto 21
19a. if motor start and run
-- measure all phase currents U,V and W
--measure all phase to phase voltages in motor connection box (U-V), (U-W) and (V-W).
20. Phase-phase voltages should be equal (+/-2%)
-if difference is higher ,
- check difference before main fuses
- check difference before contactors
- check difference before overcurrent relay
- check difference in motor cable supply side
Phase currents should be equal (+/-5%)
- if phase-phase voltages are not equal in motor connection box >> currents are not equal
- if phase to phase voltages in motor connection box are equal and currents are not >> some failure in motor
If not fail, connect load to motor and test again...
21. Fuse(s) blown >> high current short circuit or breakdown in wiring, contactors, cabling or in motor
-Overcurrent relay tripped >> if contactors and cabling are supplying all 3 phases >> some failure in motor
-Motor is stucked.
Disconnect supply to motor control ( Main switch OFF )
22. Disconnect all connections from motor windings ( cables and shorting plates)
Check insulation between windings
- Dmm high-ohm range , measure winding to winding. (U-V), (U-W) and (V-W)
....should be megaohms
Much more reliable results are obtained when High Voltage Insulation tester is used. ( Testing with 500V...750V)
23. Check resistances of windings.
- Dmm lowest-ohm range , measure windings. (U1-U2), (V1-V2) and (W1-W2)
....all should be same (+/-2%)
Much more reliable results are obtained when comparing windings inductances.
Because motor winding resistance is usually very low ,
normal DMM cant usually give reliable value for comparison windings.
One good way to test motor winding for comparison is....
-smaller ac-voltage can be used too
Here is good pictures from failures in motor windings...
Three Phase Motors - Typical Causes of Winding Failures
http://rescuemotors.com/motor windings.html