Thanks, yes, i see what you mean, though i must admit i cant foresee how the HV batteries could end up having the effect of pushing DC into the mains?......is it some kind of scenario where a car gets run over by a truck as it sits on the drive, outside the house...and then the "6mA DC in the mains" happens?The specific problem of EV OBC is possible ground fault of the DC HV circuit and lack of safe PE for the vehicle chassis,
Thanks, by "active front end" i believe you mean the diode bridge(?)active front end on an EV charger can draw currents that are not symmetric about zero current - the standard spec is < 5mA ave over 24 hrs - in the neutral - to avoid earth stake corrosion.
No. IEC 62423 specifies a minimal non-operating current of 0.5 In (3 mA).Also, its beed said that 5mA of DC leakage current in the mains is acceptable.....but EVs have to trip on 6mA.......so the DC leakage detector has to be able to differentiate between 5mA and 6mA of DC leakage current..(so it doesnt nuisance trip on 5mA) ..this would require a really expensive device?
Yes i agree, you can have down to 3mA and its got no need to trip.No. IEC 62423 specifies a minimal non-operating current of 0.5 In (3 mA).