Xerxsea
Junior Member level 1
Hello I am attempting to fix my hot tub controller. The ancient stablok gfci dual pole breaker that was in there was broken on one pole so I replaced it with a square D spa box with a gfci dual pole breaker inside, leaving that box is 2x hots(black, red) 1x neutral(white) and 1x ground.(green)
inside the box:
L1 Breaker in: Black -> SpaBox
L2 Breaker in: Red -> Spabox
L1 Breaker out: Black -> Controller
L2 Breaker out: Red -> Controller
ground bar: In and out Ground Connected
Neutral bar: In, Out, And breaker Neutral pigtail connected.
On the controller is a transformer that I believe is a step down 120v-12v transformer (google "ASSY Transformer duplex 240 sv") note it says 240v on the website but you'll notice the label says black 120v white 0v. which is how it was connected.
this feeds a bridge rectifier and powers all the finer circuitry on the control board. if this transformer is plugged in, the GFCI breaker trips immediately and I cant for the life of me figure out why.
First of all I want to make sure i'm understanding the GFCI correctly, so this is how I understand it:
The GFCI will measure leakage current on each of the 2 lines (hot and hot) and if any is leaking more than 5-10ma to ground(earth?) then it will trip.
The GFCI does not protect against overcurrent at all, so a trip is for sure leakage current.
The thing is: Ground (earth) doesn't actually connect to the PCB at all, just to the metal box the pcb is in, which in turn connects to the grounds of the pumps and whatnot.
So in my circuit current goes from black(hot) to white(neutral) via the two pins on the primary coil of the transformer. nuetral is connected to ground at the service panel, so isn't current going between black and ground then? causing the gfci to trip..? how did it work before if this is the case.
The other thought I had is I know transformers have a leakage current in themselves, is it possible the leakage current on the transformer has increased causing it to trip the gfci? I believe the previous breaker(stablok) was tripping too when the hot tub first broke a few years ago, before the stablok breaker itself broke on one pole, so i dont think it's an issue of the square d breaker being more sensitive.
attached is a board that is nearly identical (the transformer I'm mentioning is not in the picture but it connects black and white on primary side and secondary side has 2 yellow lines that feed into the rectifier at the bottom left.)
balboa53210 2500esr2
any ideas on steps i could take to troubleshoot this?
EDIT: I tried connecting only the black and the white to the transformer, and nothing else, left the transformer secondary open and it still tripped the gfci.... sooo too much leakage current in the transformer or is there an issue with running the black-neutral (120v of the 240v into the transformer primary)?
inside the box:
L1 Breaker in: Black -> SpaBox
L2 Breaker in: Red -> Spabox
L1 Breaker out: Black -> Controller
L2 Breaker out: Red -> Controller
ground bar: In and out Ground Connected
Neutral bar: In, Out, And breaker Neutral pigtail connected.
On the controller is a transformer that I believe is a step down 120v-12v transformer (google "ASSY Transformer duplex 240 sv") note it says 240v on the website but you'll notice the label says black 120v white 0v. which is how it was connected.
this feeds a bridge rectifier and powers all the finer circuitry on the control board. if this transformer is plugged in, the GFCI breaker trips immediately and I cant for the life of me figure out why.
First of all I want to make sure i'm understanding the GFCI correctly, so this is how I understand it:
The GFCI will measure leakage current on each of the 2 lines (hot and hot) and if any is leaking more than 5-10ma to ground(earth?) then it will trip.
The GFCI does not protect against overcurrent at all, so a trip is for sure leakage current.
The thing is: Ground (earth) doesn't actually connect to the PCB at all, just to the metal box the pcb is in, which in turn connects to the grounds of the pumps and whatnot.
So in my circuit current goes from black(hot) to white(neutral) via the two pins on the primary coil of the transformer. nuetral is connected to ground at the service panel, so isn't current going between black and ground then? causing the gfci to trip..? how did it work before if this is the case.
The other thought I had is I know transformers have a leakage current in themselves, is it possible the leakage current on the transformer has increased causing it to trip the gfci? I believe the previous breaker(stablok) was tripping too when the hot tub first broke a few years ago, before the stablok breaker itself broke on one pole, so i dont think it's an issue of the square d breaker being more sensitive.
attached is a board that is nearly identical (the transformer I'm mentioning is not in the picture but it connects black and white on primary side and secondary side has 2 yellow lines that feed into the rectifier at the bottom left.)
balboa53210 2500esr2
any ideas on steps i could take to troubleshoot this?
EDIT: I tried connecting only the black and the white to the transformer, and nothing else, left the transformer secondary open and it still tripped the gfci.... sooo too much leakage current in the transformer or is there an issue with running the black-neutral (120v of the 240v into the transformer primary)?