I would anticipate a holding current of just a few mA. Once the gas has ionized it will stay so until the voltage is low enough. I think 10V at 1 Amp is a measure of it's clamping voltage at that current, not an indication that it will start or sustain conduction at that voltage.
As already mentioned, a GDT is not a clamping device in the sense of a MOV or TVS, it has a 'foldback' characteristic so once ignited, it will only add about 10V to the overhead the other device sees. They are also relatively slow and I suspect you are reading the dv/dt the wrong way around, they need higher voltage to ignite them if the pulse is shorter.
The data sheet is headed with 'applications' which clearly show it is intended for signal rather than power line protection. For example you will find them in many telephone 'master sockets' to protect against static discharges on over head wires or on line modem inputs to ground for the same reason. These are all applications where they are the first line of defense but further insulation is present afterwards, not power line situations.
GDTs also suffer a degradation due to sputtering of the electrodes around the interior of the enclosure. The high temperatures of ionized gas eventually causes migration of the electrode metal to the internal surface of the chamber and reduces their ignition voltage and in extreme case can make them go completely short circuit. Look at a neon lamp that has had many hours of use (power indicator for example) and you will notice the glass has a metallic sheen and the light output has diminished. At the much higher current of a GDT discharge the effect is greatly speeded up.
Brian.
As already mentioned, a GDT is not a clamping device in the sense of a MOV or TVS, it has a 'foldback' characteristic so once ignited, it will only add about 10V to the overhead the other device sees. They are also relatively slow and I suspect you are reading the dv/dt the wrong way around, they need higher voltage to ignite them if the pulse is shorter.
The data sheet is headed with 'applications' which clearly show it is intended for signal rather than power line protection. For example you will find them in many telephone 'master sockets' to protect against static discharges on over head wires or on line modem inputs to ground for the same reason. These are all applications where they are the first line of defense but further insulation is present afterwards, not power line situations.
GDTs also suffer a degradation due to sputtering of the electrodes around the interior of the enclosure. The high temperatures of ionized gas eventually causes migration of the electrode metal to the internal surface of the chamber and reduces their ignition voltage and in extreme case can make them go completely short circuit. Look at a neon lamp that has had many hours of use (power indicator for example) and you will notice the glass has a metallic sheen and the light output has diminished. At the much higher current of a GDT discharge the effect is greatly speeded up.
Brian.