Electronic counter displays wrong count of the web on the roller

Status
Not open for further replies.

danishdeshmuk

Advanced Member level 1
Joined
Aug 17, 2011
Messages
426
Helped
35
Reputation
70
Reaction score
35
Trophy points
1,308
Activity points
4,001
Electronic counter displays wrong count of the web on the roller ....

LCM 60

if the current count is 10 it displays about 30 ..... i think it needs calibration .. what do you think ?

But how to calibrate it ? OR may it be another problem ?
 

Electronic counter displays wrong count of the web on the roller ....

-measuring what ??
-measuring principle is ??
-have you any name of device manufacturer and type ??

LCM 60 tells nothing to me.
 
www.cet-italy.it/italy/software/_fogli_istruzione/lcm60_en.pdf

CET VISUALIZED DIGITAL TOTALIZER

---------- Post added at 04:03 ---------- Previous post was at 04:01 ----------

The LCM 60 counter finds application where there is the
necessity to visualize mono-directional counts deriving
from electromechanical and logical contacts, proximity
and encoder.
 

1. Check that counter input sensor gives all the sensed and good quality pulses to count input.
- use oscilloscope to check pulse quality and level
-check inhibit signal, if inhibit is on , counter do not add counter input pulses
-if possible use parallel connected counter to check counted pulse number

2. If you are sure these two things are ok , check parameter settings.
-Input Fast - Slow.
-multiplier n1 and n2

External wiring for LCM60....
 
Last edited:
How to check parameter settings Input Fast - Slow & multiplier n1 and n2 ?

How to check inhibit signal ?

thanks
 

How to check parameter settings Input Fast - Slow & multiplier n1 and n2 ?

Everything is told in attached PDF with post #3

FRONTAL KEYBOARD DESCRIPTION
INPUT / OUTPUT DESCRIPTION
PROGRAMMING OF THE OPERATION PARAMETERS
PROGRAMMAZIONE DEI PARAMETRI DI FUNZIONAMENTO
OPERATION DIAGRAMS
CONNECTIONS & INPUT SIGNALS

How to check inhibit signal ?

Check with scope connector 6 = GND and connector 9 = signal Inhibit
 
what it should show (the scope) & what it shouldn't ?

the machine operator says that it always displays more counts than the actual ones ...... should check its parameters ?

thanks
 

what it should show (the scope) & what it shouldn't ?

1. Measure voltage between connector points 5 - 6
(6)= 0Vdc , (5) = +24Vdc +/- 20%

2. measured count pulses in point 7 should be in range (voltage in point 5) +0...-20%
-all pulses should have equal voltage and "sharp edges".

the machine operator says that it always displays more counts than the actual ones ...... should check its parameters ?

3. If parameters are not changed by somebody, there should be some fail in counted pulses.
-check from where the pulses are generated ( is there any proximity sensor for
sending count pulses , check is adjusting there correct )

4. If you must change parameters ,
remember to write down the original values first.
( parameters n1 and n2 are counter multipliers )
 
Last edited:
yeah there's a sensor , i think its a proximity sensor
 

The name of the sensor is Magnetschalte 100 VA, 250 v , 2A ... Typ GMS 9

Heinrich Kubler AG baar
025340

---------- Post added at 22:49 ---------- Previous post was at 22:45 ----------

Magnetschalter 100 VA, 250 v , 2A ... Typ GMS 9

Heinrich Kubler AG baar
025340


There are only 4 wires connected to the LCM 60 counter

at terminal 3 : 110 VAC
at terminal 4 : 0 VAC
at terminal 5 : + 24 Vdc 80mA
at termial 7 : Input

and its selected in pnp configuration ....

Now how to check the inhibit signals & other things to be checked which you mentioned in the above post ? Should i follow the same steps & the same patterns in this condition , as you mentioned above ?

thanks
 

This sensor is Magnetic Proximity Switch ,
active switching element is reed-switch.

Sensor is 2-wire type , connected between terminals 5 and 7

It is typical when they get older, this type of switch can give the uncertain
contact and thus cause a false pulse number
- bad contact = too low pulse number
- contact vibrating = too high pulse number

KSR Kuebler Catalog 1008....
General info in pages 3...6
Kuebler GMS 9 in page 9
http://www.ksr-usa.com/download/1008.pdf

Now how to check the inhibit signals

If there is only 5-7 connected , check only count pulses ( 6 - 7)
and 24Vdc supply (5-6)

pnp configuration is right.

the machine operator says that it always displays more counts than the actual ones

I guess bad contacts ( vibrating ) , so i would replace sensor.
 
can i test this sensor ? If so, then how to ?
 

As i wrote in post#8

1. Measure voltage between connector points 5 - 6
(6)= 0Vdc , (5) = +24Vdc +/- 20%

2. measured count pulses in point 7 should be in range (voltage in point 5) +0...-20%
-all pulses should have equal voltage and "sharp edges".

- all pulses should have equal lenght.

Use oscilloscope for checking pulses.

 