Dual active bridge core saturation

Status
Not open for further replies.

Techman_7

Full Member level 2
Joined
Dec 21, 2013
Messages
138
Helped
0
Reputation
0
Reaction score
1
Trophy points
1,298
Activity points
2,420
If the dual active bridge topology is to be operated in bidirectional mode, then the DC blocking capacitor is placed in series with transformer winding to avoid core saturation.
Does this DC blocking capacitor is need in both primary & secondary windings of transformer?
Pls refer below topology schematic with only 1 DC block cap in primary.

 

Unless your control ( on the RHS ) ensures no build up of net DC current in the Tx pri - you need the blocking cap on both sides.
 