[SOLVED] Current Transformer High Resistance Burden - No Flames?

Status
Not open for further replies.

coates

Member level 1
Joined
May 20, 2013
Messages
38
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,286
Visit site
Activity points
1,660
Hi all,

I'm trying to understand current transformers better. A precaution that one can't avoid when reading about CTs is the open-circuit burden. Everyone says it's very dangerous and I've watched videos of CTs bursting into flames because of it.

I thought I'd test this out in a controlled environment. I wound about 300 turns onto a small core (1.5" O.D. toroidal) I had lying around, stuck a cable through it and ran 150 amps through it. Nothing happened -- no flames, no smoke, no arcing.

I did carefully rub the wire ends against each other and got arcs, however, so I knew something was happening. I put an 10:1 oscilloscope on the terminals and got the theoretical peaky waveform with peak voltages of about 600V.

What is happening here? My theory is that the enamel insulation or a component is breaking down at 600V but there is no smoke because not much power is being transferred by the CT.

Can anyone shed some light on this?

Many thanks.
 

There are two possible failure modes:
- winding insulation breakdown with flashover
- core overheating due to saturation losses

Your experiment was probably too short to observe the latter case.
 
Reactions: coates

    coates

    Points: 2
    Helpful Answer Positive Rating
Thanks FvM.

Do you know if the flashover would be visible? Also, would it develop into something more dangerous if it was left like this?
 