the question is simple. At maximum rating of CT you have 5amps. So the resistor must be P=I^2*r=25*1 =25watt. But i suppose the nominal current which have will be about 20 -100 amps. So the transformer will give you 1amp at burden resistor. So the wattage will be drop to P=1^2*1=1watt.
Current transformers have a power rating specification, which defines the maximum burden resistor. It's unlikely that a standard 500A CT has more than 5 or 10 VA rating. You get better accuracy by using a lower burden value.
In any case, you can't give the AC output voltage of the burden directly to a PIC ADC, in so far the voltage calculation isn't right. And you have to consider that 5V rms is about 14 Vpp for sine voltage.
Have you seen CT's by ABB. They have a broad range. You can measure current passing through a wire by contactless method. As it is done in clamp meters.