I share your concern FlapJack.As a general rule switching power supplies have the - terminal referenced to earth ground. If you try to put two of these is series they will fight each other, as the minus terminal from the two supplies are both probably connected to case/earth ground.
That's definitely not true for general purpose SMPS. The maximum output common mode voltage against PE is of course restricted, but surely no problem for 2 x 24V series connection. For the linked Astrodyne SMPS output isolation strength is e.g. 500 VAC.As a general rule switching power supplies have the - terminal referenced to earth ground.
Respectively both devices should have their PE connected, will be usually already achieved by mounting the metal case.
Ground BOTH metal chassis to each other and mains earth.
Its a safety requirement and will have absolutely no effect on operation.
Good point.It is highly recommended to add the anti-parallel diodes. 10A diodes are OK.
In case of exceeding the current limit the supply with the lower current limit can have its output reversed and get damaged.