Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Choosing Battery Capacity

Status
Not open for further replies.

SphinX

Advanced Member level 3
Advanced Member level 3
Joined
Jan 25, 2002
Messages
822
Helped
58
Reputation
116
Reaction score
29
Trophy points
1,308
Location
EGYPT
Activity points
7,045
Salam,

For Sealed Lead Acid Battery

Specifying battery capacity involves a bit more than multiplying the load current by the backup time in hours. You must first de-rate the battery for capacity tolerance, temperature, and discharge rate.


First, multiply the average load current by the backup hours of operation you need.

Next, add 15% to cover loss of capacity from tolerance and UN-cycled batteries.

For every 10C (16F) below room temperature (72F) your worst case low temperature is add 10%.

If your back-up time is less than 20 hours, add 10% for every time you have to double your back-up time to equal more than 20 hours.

An example may help:
20 minutes would have to be doubled 6 times to equal more than 20 hours. Thus you would have to add 60% on to your required capacity.
Finally, add 40% to provide for an economic life cycle. A battery with 60% of its capacity left is considered worn out.


Example
10 Hours @ 200 MA, average current, worst case temp is 0C
10 hour back-up time at .2 Amperes 2.0 AH
15% from step 2 .3 AH
0C add 20% from step 3 .4 AH
Add 10% from step 4 .2 AH
add 40% from step 5 .8 AH


Total 3.7 AH

Bye
 

There is a battery bank sizing worksheet at
h**p://www.nooutage.com/battery.htm

Also, similar worksheets are present.
 