Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Change sensor's common to low!!!

Status
Not open for further replies.

auto_mitch

Full Member level 3
Full Member level 3
Joined
Oct 14, 2004
Messages
172
Helped
16
Reputation
32
Reaction score
3
Trophy points
1,298
Activity points
1,240
Hi.
i have a problem with a pressure sensor. The sensor output is 4-20mA.
The common of the output is at high (+24V). I want to change the common to low (0V, GND) to plug the sensor to plc.
Could u help me???
 

Normally you should run pressure transducer of +V (in your case 24Vdc) and inside your PLC you will find 250 ohm termination resistor which is used for 1(4mA)-5(20mA)V range and that is typical configuration.
If you want to run it of 0V check if your plc has differential inputs. If it has check in specification what is max common voltage for these inputs and if it is above 24Vdc connect negative pol of pressure Tx to 0V, positive pol to 250 ohm(or other, depending on gain, range etc..) resistor and the other end of resistor to 24Vdc and measure voltage across this resistor.
'If you want to decrease levels you can connect another resistor betwenn 250 ohm and 24Vdc but make sure that your pressure Tx operates within its operating voltage range (usually min voltage will be somewhere around 10Vdc)
It is not good practice but can be done... 8)
 