I have a local centre tapped transformer 12V and 12V. There is no current rating labelled on it. (it is just about a little smaller than the size of a tennis ball). I guess it should be 1 Amp.
Is there a way to find out actual current rating of a transformer?
Dear furqankaimkhani
Hi
Yes there is a simple way available : your transformer has a core . it can be EI , core . if yes , EI< or = 30 sqrt ( AFE ) and AFE = 1.2 sqrt (P1) P1 =Vin* Iin . so you have vin , and you have vout , you will fine I in from that formula as well , and then you will find iout ( approximately ) with this formula : Vo/Vi = Io/Ii .
Best Wishes
Goldsmith
I have a local centre tapped transformer 12V and 12V. There is no current rating labelled on it. (it is just about a little smaller than the size of a tennis ball). I guess it should be 1 Amp.
Is there a way to find out actual current rating of a transformer?
Yes, like additional to Goldsmith post, you can use nonius instrument to measure diameter of wire on secundar and see what current can be supported by that wire. Sometimes core is bigger and wire diameter is smaller to make lower temperature. ;-)
I mean 3 to 5, if you select 2.5, it is better, however your bobbin has enough room to wound wire, if not, your coil is too fat to be assembly with core.
I mean 3 to 5, if you select 2.5, it is better, however your bobbin has enough room to wound wire, if not, your coil is too fat to be assembly with core.
Usually what I know calc is for 2,5A/mm² and 3,5A/mm² over that like 5A/mm² I think we need oil cooling.
I think that is better for existing unknown trafo specification consider lower parameters, based on core square area and wire diameter based on up to 2,5A/mm² amperage density.
Also if density higher per mm² of wire, temp will rise and losses will be higher. Higher amperage per mm² of wire also require better isolation of wires and each turn of winding need isolation resistive on high temp. Wires must be several times protected with special high temp lacquer.
My opinion is to threat unknown trafo as 60-75C temp, not 150C or over.