What is your actual DC bus voltage? At a minimum at 400 V @ 15KW, the current will be 38A, so the ripple current could be 3 times this, say 100A. So the secret is to keep the capacitors cool and to share the ripple current equally among them. So as a ball park figure, using 200 MFD caps , you need 19 X 5 = 195 caps ( I would use 200). Another point to bear in mind is that if a capacitor goes short circuit, it might explode or if it does not you will have to unsolder them one by one until you find it. So I would wire , say 5 in a star configuration (equal length leads), with a red 4mm socket and a black 4mm socket as the centre or star points. Using thick flex with 4mm red and black plugs, connect from the star points to the bus. All these leads should be the same length. A decent 4mm plug and socket should handle 10A! Remember cooling!! !!
Frank
Did you ever see an inverter or similar device with a similar passive discharge circuit involving a ridiculous 5% efficiency loss?The lower the value of resistor, the quicker the capacitor discharges, but the more power wasted (and heat generated). to get from the 320 to 50V in time T, this is when C X R = .5T (about), so if you think 10 Seconds is a reasonable time, then C X R = 5 Seconds so R = 5/200 M ohms or 25 k, the power dissipated in each resistor will be 320 X 320/25K = 4 W, there are 195 of them so that is 800 W ( fan required).
First with a bus voltage of 320 V @ 15 KW, I = 15000/32 = 500 A!! the purpose of the resistor across the capacitor (bleed resistor) is to discharge the capacitor, so that when the unit is switched off (for working on), there are no dangerous voltages stored on the capacitors. The lower the value of resistor, the quicker the capacitor discharges, but the more power wasted (and heat generated). to get from the 320 to 50V in time T, this is when C X R = .5T (about), so if you think 10 Seconds is a reasonable time, then C X R = 5 Seconds so R = 5/200 M ohms or 25 k, the power dissipated in each resistor will be 320 X 320/25K = 4 W, there are 195 of them so that is 800 W ( fan required).
Frank
load = 5KW, =V X V/R , R = 320 X 320/5000 = 100,000/5000 = 20 ohms. So putting your 20 ohm load onto your .19F capacitor will cause it to discharge, so after 3.8 Secs the voltage will have fallen to .37 X 320 V ~ 100V.
Frank