hm_fa_da
Full Member level 5
Hello,
There is a disagreement between me and a friend on the below problem:
In IEC60079-11 Standard (For ATEX intrinsically safe section), Page 47, 5th paragraph mentions:
"If a current-limiting device is necessary to limit the prospective current to a value not greater
than the rated breaking capacity of the fuse, this device shall be infallible in accordance with
Clause 8 and the rated values shall be at least:
– current rating 1,5 × 1,7 × In;
– voltage rating Um or Ui;
– power rating 1,5 × (1,7 × In)2 × maximum resistance of limiting device."
The simple circuit schematic is as below:
As you see, the maximum input Ui is 3.9V, there is a 3A fuse in series with 1.2 Ohm resistor. for calculating the rating of the resistor, i say the maximum possible short circuit current is limited to I = V/R => Isc = 3.9V/1.2 Ohm = 3.25A.
( I know we should consider resistor tolerance and ... )
So considering safety factor of 1.5, the current rating of resistor should be at least :
1.5 x 3.25A = 4.875A.
But My freind says according to the quoted note from standard (Page 47, 5th paragraph) we should use In of the fuse and the 1.7 factor instead of calculated short circuit current (V=I x R ...),
So the resistor rating is :
1.5 x 1.7 x 3A = 7.65A ...
I think when the Maximum possible current in the circuit is 3.25A, why we should calculate more current value (1.7 x 3A) (safety factor of 1.5 will be used for both values) !
If we don't use any fuse, then the only solution to calculate maximum short circuit current is Vmax / R = 3.25A, so adding a fuse can not increase the current limitation !
another example is using a i.e 100A fuse, then according to my friend opinion the 1.7 x 100A = 170A should be calculated in current rating of the resistor in series with the fuse !
What's your vote ?
Thanks & Regards.
What's your vote ?
Thanks & Regards.